I am an electrician in Washington state and have a customer who wants me to install some EZ read meter bases that are not UL listed but they are ANSI certified. Is ANSI considered as safe in electrical equipment as the UL listing?
Washington is one of the states that does not specifically say 'UL", but requires what is referred to as "NRTL listing". NRTL means Nationally Recognized Testing Labs. There is a list of acceptable NRTLs maintained by OSHA that you can access on the Web by searching on "OSHA NRTL list". Washington state will accept any of those testing labs.
ANSI, as mentioned above, is a standards writing organization, not a testing lab. So if your meter mfr is trying to imply that the meter is "ANSI Certified" he is either a liar or you are not getting the whole story. There is no such thing as "certification" by ANSI. Maybe, just maybe, he is trying to say that they, the meter mfr, is "certifying" that their meter is built to ANSI specifications, but that is kind of like saying "I, Mr. Fox, hereby certify that there are no predators in this hen house". In other words, let the buyer beware. But the only benefit of doubt I'll give them is that maybe they have gone to some OTHER lab to have the meter tested and certified to have met ANSI specifications (see below). If so, and that lab is on the NRTL list, you MIGHT be OK.
ANSI has only one specification for "meters" that I can find, C12 for "energy metering", including "smart grid" metering. The ANSI spec calls out standards for metering accuracy and performance, as well as different classes for accuracy attainment. So saying a meter
MEETS ANSI C12 is a marketing claim, until someone else (known as a "3rd party", like a testing lab) backs it up with a test report. But I do not believe the ANSI spec is related to product SAFETY anyway, which is what UL and other NRTL testing as required by the State would be about.
So bottom line, I seriously doubt your meter is going to be allowable if that's all they can say about it.