If I have two panelboards at two opposite walls of a building 25ft apart. And the Electrical Sercive enters at Panelboard#1 with MCB where the neutral is grounded. A sub feed goes from this panelboard#1 to another Panelboard#2 also with a MCB where the neutral is grounded. There is no EGC connection between these two panel. The conduit is PVC.
Is it okay? If not okay what are the reasons.
The usual way of doing it is that at Panelboard#2 the neutral has to be seperated from Ground and running a EGC conductor between the two panelboards.
Is it okay? If not okay what are the reasons.
The usual way of doing it is that at Panelboard#2 the neutral has to be seperated from Ground and running a EGC conductor between the two panelboards.