We have solar array with a single SMA Tripower Core1 33 kW inverter. The inverter goes to a small pad mount 45 kVA 480/208 step down transformer. Apparently we ended up with a transformer with delta on the 480 side, and the inverter is only compatible with 480/277 wye.

Is there a way to get this inverter working? Is our only option to replace the transformer?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Your only option is to replace the transformer.

Seems like you got the opposite of what you need. You got a 480D to 208Y 'step down' transformer. What you most likely want is a 208D to 480Y 'step up' transformer. At any rate, the manufacturer should approve of the 208 side being the side that energizes the transformer from the utility.

Good luck.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Whats the make and model? You (or somone) can probably can just reconfigure it.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Whats the make and model? You (or somone) can probably can just reconfigure it.
I have never seen a non-custom transformer that can be field reconfigured.

In my experience the secondary windings are almost always welded at the factory. Then there is the need to change the winding voltage ratio by a factor of 1.73.
 

shockking

Member
Location
Sacramento, CA
Occupation
engineer
Thanks all for the replies, much appreciated.

TLDR; after digging, my options are:
1) replace the 480D - 208Y/120 with a 480Y - 208Y/120, for which I was quoted $3.5k installed and 5 week lead time; or
2) add a second transformer, 480Y - 480D, quoted $4.8k installed with 3 day lead time.

The transformer we installed is:
ACME Electric general purpose Low Voltage Distribution Transformer - Three Phase, 480Δ - 208Y/120V, 45kVA
(catalog ID: T3045K0013B)

Seems in theory maybe it could be reconfigured from delta to wye... but I have not come across anyone who's ever heard of it being done. I'm betting @jim dungar is right that all else aside, the windings are likely factory welded in place (not field serviceable).

There's a short 50-foot run from the inverter to the interconnection. The building's service at the POI is 208Y/120. Output from the inverter 480/277 wye. The design intent was to run the 50-feet at 480V 3P3W (no neutral) to a step down transformer, and tie in from there. I don't think the engineer or electrician have much experience with solar and just overlooked that the inverter was wye only.

Two questions linger for me...
1) I don't fully understand what the issue is for the inverter; why does the inverter care if it's delta or wye? What measurement is there that it is able to tell the difference?
(note: the inverter can be used with our without neutral, but must be wye. It arrived from the factory with a bridge between the neutral terminal and the enclosure/ground for use without a neutral conductor to the POI.)

2) what should I do with this transformer if I replace it? It can't be returned now that we've punched holes in it... Ebay/craigslist? Anyone here want it?
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
This one says they have it in stock, but you'd need to verify that:


Adding a second transformer would add unnecessary losses and complexity, take extra room, etc.
 

dkidd

Senior Member
Location
here
Occupation
PE
We have solar array with a single SMA Tripower Core1 33 kW inverter. The inverter goes to a small pad mount 45 kVA 480/208 step down transformer. Apparently we ended up with a transformer with delta on the 480 side, and the inverter is only compatible with 480/277 wye.

Is there a way to get this inverter working? Is our only option to replace the transformer?
Zig-zag transformer to get a neutral?

 

Carultch

Senior Member
Location
Massachusetts
1) I don't fully understand what the issue is for the inverter; why does the inverter care if it's delta or wye? What measurement is there that it is able to tell the difference?
(note: the inverter can be used with our without neutral, but must be wye. It arrived from the factory with a bridge between the neutral terminal and the enclosure/ground for use without a neutral conductor to the POI.)

This particular inverter requires 277V to ground to operate, and its internal relay settings are based on the phase-to-neutral voltage. It can do its measurements from line-to-ground, so that you don't necessarily need to bring a neutral to it to properly function. However, it still needs the WYE grid in order to avoid the possibility of its components experiencing 480V to ground. While an inverter in general could be built with robust components to operate with 480V nominal to ground as is the most extreme you'll get on an ungrounded delta grid, this particular inverter isn't built for it. Its internal relay settings have a maximum amount you can adjust them to avoid overloading its internal components, and come standard with settings based upon the 277V value in a nominal 277/480V grid.

An ungrounded delta grid will not maintain the three phase voltages to be "equidistant" from ground. On occasion, the "triangle" may be centered, but it will not maintain this with enough stability to allow the inverter to operate. In order to ground the center of an existing ungrounded delta grid, you'd need a zigzag transformer or grounding transformer, to be used for establishing the neutral point as a reference to ground.
 