Is it required to have a local disconnect switch for a 480V Outlet

Status
Not open for further replies.

EEPithon

Member
Location
80128
Occupation
Electrical Engineer
Installing 480V outlets outside at a commercial site, but I was wondering if these needed to have a local disconnect switch for each outlet based in the NEC code. I cannot find anything, but want to make sure I am not missing something. The outlet is rated 480V 3PH 30A.
 
Is it a 480V receptacle or is it hard wired to a device? If it's a receptacle, unplugging the device counts as a proper disconnect method.

I'm assuming you can turn the device completely off before disconnecting. I wouldn't want to disconnect under load. In that case, I would add a disconnect switch.
 
Is it a 480V receptacle or is it hard wired to a device? If it's a receptacle, unplugging the device counts as a proper disconnect method.

I'm assuming you can turn the device completely off before disconnecting. I wouldn't want to disconnect under load. In that case, I would add a disconnect switch.
It is a receptacle.
 
Some of them are interlocked devices...you have to insert the plug before you turn the disconnect on, and you can't remove the plug until you turn the disconnect off.
 