Is it required to have a local disconnect switch for a 480V Outlet

Status
Not open for further replies.

EEPithon

Member
Location
80128
Occupation
Electrical Engineer
Installing 480V outlets outside at a commercial site, but I was wondering if these needed to have a local disconnect switch for each outlet based in the NEC code. I cannot find anything, but want to make sure I am not missing something. The outlet is rated 480V 3PH 30A.
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
Is it a 480V receptacle or is it hard wired to a device? If it's a receptacle, unplugging the device counts as a proper disconnect method.

I'm assuming you can turn the device completely off before disconnecting. I wouldn't want to disconnect under load. In that case, I would add a disconnect switch.
 

EEPithon

Member
Location
80128
Occupation
Electrical Engineer
Is it a 480V receptacle or is it hard wired to a device? If it's a receptacle, unplugging the device counts as a proper disconnect method.

I'm assuming you can turn the device completely off before disconnecting. I wouldn't want to disconnect under load. In that case, I would add a disconnect switch.
It is a receptacle.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Some of them are interlocked devices...you have to insert the plug before you turn the disconnect on, and you can't remove the plug until you turn the disconnect off.
 
Status
Not open for further replies.