Calrissian45
Member
- Location
- Southern California
- Occupation
- Electrical Engineer
I have a project that will need to pull two 1/0 medium voltage cables through twelve 3'W x 5'L x 3.5'H handholes a total distance of 3,384 feet. The max distance between hand holes is 400 feet. I used the SIMpull Cable Pull Calculator to determine that it could theoretically be done in two pulls with one splice in the middle. I'm not sure if that's how a contractor would actually do it though.
Pull 1:
Length = 1,691 ft
Continuous Tension = 1,483 lb
Max Sidewall Pressure = 597 lb
Handhole Qty = 7
Pull 2:
Length = 1,693 ft
Continuous Tension = 1,026 lb
Max Sidewall Pressure = 5 lb
Handhole Qty = 5
Pull 1:
Length = 1,691 ft
Continuous Tension = 1,483 lb
Max Sidewall Pressure = 597 lb
Handhole Qty = 7
Pull 2:
Length = 1,693 ft
Continuous Tension = 1,026 lb
Max Sidewall Pressure = 5 lb
Handhole Qty = 5