jkruse
Member
- Location
- Pennsylvania
- Occupation
- Mechanical Engineer
I’m getting conflicting information on an engineering plan that uses Multiwire Branch Circuits and the Neutral Conductor clause of 310.15 (B) (5) to keep the current carrying conductor count low for conduit derating. The conflict revolves around whether a MWBC is a “single circuit” as required in 310.15 (B)(5)a and how to apply the “shall be permitted” portion of 210.4 (A) allowing a MWBC to be considered multiple circuits.
210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits...
310.15 Ampacities for Conductors Rated 0–2000 Volts.
(B) (5) Neutral Conductor.
(a) A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(3)(a).
In 225.30, this is clearly defined for outside branch circuits, but other sections are silent.
225.30 Number of Supplies.
A building or other structure that is served by a branch circuit or feeder on the load side of a service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.
My hunch is the 210.4 (A) note is intended to clarify that the separate branches can be counted individually for locations requiring a particular circuit count (ie. kitchen receptacles). If a MWBC can always and arbitrarily be considered “multiple circuits”, how would 310.15 (B) (5) be of practical use?
Technical drawbacks of MWBC aside, is there further clarification of a “single circuit” applicable to 310.15 elsewhere in NEC?
Note code references are 2017 NFPA 70/ 2018 IRC
210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits...
310.15 Ampacities for Conductors Rated 0–2000 Volts.
(B) (5) Neutral Conductor.
(a) A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(3)(a).
In 225.30, this is clearly defined for outside branch circuits, but other sections are silent.
225.30 Number of Supplies.
A building or other structure that is served by a branch circuit or feeder on the load side of a service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.
My hunch is the 210.4 (A) note is intended to clarify that the separate branches can be counted individually for locations requiring a particular circuit count (ie. kitchen receptacles). If a MWBC can always and arbitrarily be considered “multiple circuits”, how would 310.15 (B) (5) be of practical use?
Technical drawbacks of MWBC aside, is there further clarification of a “single circuit” applicable to 310.15 elsewhere in NEC?
Note code references are 2017 NFPA 70/ 2018 IRC