Need some help settling some things.
My boss is at his ?lake house? for the week fishing. He left me (a first year apprentice) and ?Steve? (my new boss for the week) to finish a small residential panel upgrade job. He?s made some questionable decisions that I don?t think are right. Thought you guys could help me, he gets VERY defensive when questioned, even when I bust out the NEC?we get inspected in 2 days and I was trying to impress my boss with a clean pass.
The situation:
SE cable (AL 2/0) drops into attic, runs to meter on back of house, then feeds the distribution panel 25? away (through crawlspace) inside the garage on the front of the house. No service disconnect at the meter or main breaker on panel. Only GEC (#6 copper) is to cold water line coming out of water heater. No grounding rods at the meter either.
The homeowner wants to add two additional 20A circuits for a new sump pump in the crawlspace, and landscape lightning in the backyard, etc. The old Cutler Hammer 150A panel was full and showing serious signs of age. We replaced it with a larger SquareD 200A panel with tons more space. Code requires a disconnect near the meter, so we replaced the old rusty meter box with a dual combination service entrance device. We?re using a 150A breaker in the dual box since we want to keep the AL 2/0 SEC, and not fish 4/0. The house is very small and wouldn?t pull 200A anyway?
Everything is installed, panel is beautifully organized, and we?ve added two ground rods at the meter 6? apart. Then Steve said, ?I forgot to add the green bonding screw in the panel.? He installed it.
???
I have 3 questions:
1. When you have a service disconnect ?upstream? (as in next to our meter) you leave the green ?bonding screw? OUT of the panel, correct? To keep neutral and ground separate? (the panel is considered a ?sub panel? now correct?) The SquareD dual combo box has its grounding and neutral terminal lugs on the same mounting bar that?s bonded to the box anyway. (250.24)(B)?? THIS is where the bonding happens, right. Am I wrong here? Steve says I am wrong.
2. Steve also says that we don?t need to run an EGC (#6 copper) from the newly installed service disconnect at the meter to the dis. panel?s ground bar, since we have the bonding screw installed in the panel?? I?m pretty sure this ground line needs to be installed.
3. We still only have one GEC, grounded to the water line. Doesn?t section 250 explain all of this? Doesn?t the distribution panel require 2 points of ground? Don?t we need to add another ground rod in the crawlspace directly behind the dis. Panel. Again, Steve says, ?No?
Sorry to vent here, I?m a little upset. I?ve been working very hard and trying to learn everything I can. Some people are just difficult to work with I guess. Or maybe I?m just being a know-it-all disrespectful punk. I tried to find the references in the NEC to show him, but the new changes in article 250 in terms of grounding/bonding are still confusing to me. If I?m wrong in my understanding, please enlighten me, I can be humble. I?ve seen it done.
I can?t believe how much there is to learn. I have developed GREAT respect for the older guys who spout out half the NEC from memory?any help is much appreciated!!!
Scott
My boss is at his ?lake house? for the week fishing. He left me (a first year apprentice) and ?Steve? (my new boss for the week) to finish a small residential panel upgrade job. He?s made some questionable decisions that I don?t think are right. Thought you guys could help me, he gets VERY defensive when questioned, even when I bust out the NEC?we get inspected in 2 days and I was trying to impress my boss with a clean pass.
The situation:
SE cable (AL 2/0) drops into attic, runs to meter on back of house, then feeds the distribution panel 25? away (through crawlspace) inside the garage on the front of the house. No service disconnect at the meter or main breaker on panel. Only GEC (#6 copper) is to cold water line coming out of water heater. No grounding rods at the meter either.
The homeowner wants to add two additional 20A circuits for a new sump pump in the crawlspace, and landscape lightning in the backyard, etc. The old Cutler Hammer 150A panel was full and showing serious signs of age. We replaced it with a larger SquareD 200A panel with tons more space. Code requires a disconnect near the meter, so we replaced the old rusty meter box with a dual combination service entrance device. We?re using a 150A breaker in the dual box since we want to keep the AL 2/0 SEC, and not fish 4/0. The house is very small and wouldn?t pull 200A anyway?
Everything is installed, panel is beautifully organized, and we?ve added two ground rods at the meter 6? apart. Then Steve said, ?I forgot to add the green bonding screw in the panel.? He installed it.
???
I have 3 questions:
1. When you have a service disconnect ?upstream? (as in next to our meter) you leave the green ?bonding screw? OUT of the panel, correct? To keep neutral and ground separate? (the panel is considered a ?sub panel? now correct?) The SquareD dual combo box has its grounding and neutral terminal lugs on the same mounting bar that?s bonded to the box anyway. (250.24)(B)?? THIS is where the bonding happens, right. Am I wrong here? Steve says I am wrong.
2. Steve also says that we don?t need to run an EGC (#6 copper) from the newly installed service disconnect at the meter to the dis. panel?s ground bar, since we have the bonding screw installed in the panel?? I?m pretty sure this ground line needs to be installed.
3. We still only have one GEC, grounded to the water line. Doesn?t section 250 explain all of this? Doesn?t the distribution panel require 2 points of ground? Don?t we need to add another ground rod in the crawlspace directly behind the dis. Panel. Again, Steve says, ?No?
Sorry to vent here, I?m a little upset. I?ve been working very hard and trying to learn everything I can. Some people are just difficult to work with I guess. Or maybe I?m just being a know-it-all disrespectful punk. I tried to find the references in the NEC to show him, but the new changes in article 250 in terms of grounding/bonding are still confusing to me. If I?m wrong in my understanding, please enlighten me, I can be humble. I?ve seen it done.
I can?t believe how much there is to learn. I have developed GREAT respect for the older guys who spout out half the NEC from memory?any help is much appreciated!!!
Scott