I try to keep an open mind and we are all here to learn.Originally posted by unsaint34:
Please be open minded about why I still think my house might be a separately derived system. (I'm not trying to prove anyone wrong. I just wanted to learn accurately.)
Considering the NEC stops at the service point...90.2 Scope.
(B) Not Covered. This Code does not cover the following:
(5)Installations under the exclusive control of an electric utility where such installations
a.Consist of service drops or service laterals, and associated metering, or
b.Are located in legally established easements, rights-of-way, or by other agreements either designated by or recognized by public service commissions, utility commissions, or other regulatory agencies having jurisdiction for such installations, or
c.Are on property owned or leased by the electric utility for the purpose of communications, metering, generation, control, transformation, transmission, or distribution of electric energy.
...in my opinion it is wrong to try to apply NEC definitions to equipment beyond the service point.Service Point. The point of connection between the facilities of the serving utility and the premises wiring.
Just an observation: If it is truly isolated, it would be the first one I ever saw. Our utility guys could better speak to this than I, but, my understanding is all single phase, residential utility xfmrs are bonded from the primary neutral to the secondary neutral (high probability of oddball exceptions noted).Originally posted by unsaint34:
... The tranformer that feeds my house is a isoltation transformer, which means that the secondary and the primary has absolutely NO electrical connection. ...
Note to iwire: There isn't much difference in the grounding between the two is there? Don't both use table 250.66?Originally posted by iwire:
... 250.24 Grounding Service-Supplied Alternating-Current Systems or do we follow 250.30 Grounding Separately Derived Alternating-Current Systems ...
Carl your right the rules are similar but they are not the same.Originally posted by coulter:
Note to iwire: There isn't much difference in the grounding between the two is there? Don't both use table 250.66?Originally posted by iwire:
... 250.24 Grounding Service-Supplied Alternating-Current Systems or do we follow 250.30 Grounding Separately Derived Alternating-Current Systems ...
And so are our SDS's. Maybe not as directly but the primary grounded conductor is bonded to the secondary grounded conductor via the equipment grounding conductors and the main/system bonding jumpers.Just an observation: If it is truly isolated, it would be the first one I ever saw. Our utility guys could better speak to this than I, but, my understanding is all single phase, residential utility xfmrs are bonded from the primary neutral to the secondary neutral (high probability of oddball exceptions noted).