This seems to be an ongoing issue and source of confusion for many. I am in a fight right now with an inspector regarding this. I have a delta-wye, 112.5KVA, 3 phase transformer feeding a 400A rated panel with a 400A main breaker.
My secondary conductors between the panel and the transformer are 4#600KCM, #1/0G. The #600KCM conductors are rated at 420A assuming 75 degree rated terminations. The inspector is telling me that unless I can prove with a third party inspection that there is no current on the neutral, I have to derate my secondary conductors and upsize them to an absurd (2) x 4#300KCM.
The NEC seems pretty clear in Article 310.15(B)(4)(a) that the neutral that "carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(2)(a). 310.15(B)(4)(c) does say that if the "major portion of the load consists on nonlinear loads" the neutral shall be considered a current carrying conductor. But my panel is not feeding a data center or a computer room. It's mostly pumps and motors.
I mean to fight this requirement and think that this inspector is confused. What do you guys think?
My secondary conductors between the panel and the transformer are 4#600KCM, #1/0G. The #600KCM conductors are rated at 420A assuming 75 degree rated terminations. The inspector is telling me that unless I can prove with a third party inspection that there is no current on the neutral, I have to derate my secondary conductors and upsize them to an absurd (2) x 4#300KCM.
The NEC seems pretty clear in Article 310.15(B)(4)(a) that the neutral that "carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(2)(a). 310.15(B)(4)(c) does say that if the "major portion of the load consists on nonlinear loads" the neutral shall be considered a current carrying conductor. But my panel is not feeding a data center or a computer room. It's mostly pumps and motors.
I mean to fight this requirement and think that this inspector is confused. What do you guys think?