S skyline77 Member Jul 28, 2020 #1 Hi, For a three-phase y-connected solidly grounded system is the neutral conductor considered a grounded conductor or not?
Hi, For a three-phase y-connected solidly grounded system is the neutral conductor considered a grounded conductor or not?
busman Senior Member Location Northern Virginia Occupation Master Electrician / Electrical Engineer Jul 28, 2020 #2 Yes, but it sounds like a trick question.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 28, 2020 #3 skyline77 said: Hi, For a three-phase y-connected solidly grounded system is the neutral conductor considered a grounded conductor or not? Click to expand... Do you want me to change the thread title?
skyline77 said: Hi, For a three-phase y-connected solidly grounded system is the neutral conductor considered a grounded conductor or not? Click to expand... Do you want me to change the thread title?
ron Senior Member Location New York, 40.7514,-73.9925 Jul 28, 2020 #4 For a three-phase y-connected solidly grounded system, the derived neutral is how it becomes a grounded system, and thus it is the grounded conductor.
For a three-phase y-connected solidly grounded system, the derived neutral is how it becomes a grounded system, and thus it is the grounded conductor.