Some insight...
Some insight...
don_resqcapt19 said:
mxslick,
Did that equipment have an EGC?
Yes sir it did, However, out of eleven failures of that kind in the field, four happened with the grounding pin on the cords cut off. Of those four, three were sitting on their metal feet directly on a concrete floor slab, so I'd say that would have made a fair path to ground, one was on carpet layed (lain?) over vinyl tile, so maybe a so-so path there.
Edited to add: No part of the control circuit or low voltage supply was connected in any way to the egc.
I used to repair those control modules, and have the power supply, one platter arm and motor as a test set-up (the complete system has one power supply and three arms/motors.)
For giggles I set up a test and sacrificed a few modules. One test was with hot/neut reversed and egc connected, the burnout happened within 10 seconds.
In the second test I lifted the EGC with a ground lift adapter. The failure happened, but it took about 30-45 seconds with some rather strange noises from the motor.
The entire rig was sitting on rubber pads on my wood workbench.
Unfortunately I did not think to measure voltage from the egc to ground in those tests.
My conclusion from those tests and results was that it was a very poor design, but the actual failure mode was difficult to track, as the modules used LEDS and photocells, with a moving cam to regulate the light (and thus the speed of the motors), and the control arm had to be fully enclosed and light-tight to do any testing. The failures always resulted in almost total destruction of all the components, so it was difficult to tell what failed first and what followed in what order.
Goo49:
I can agree partly with this part of your post:
Yup. With only a two conductor suppy cord, being fed from an Alternating Current source, the only thing that happens when the supply conductors are reversed, is that the directional flow that you think may have caused this failure, got there a half cycle sooner. Or maybe later.
Again, I stand by my supposition (and the results of my "no egc" test above) in that the issue is not when the half-cycle happens, but the fact that a part that is supposed to be referenced to neutral in whatever form was subjected to the line voltage instead, and capacitive coupling to earth created enough voltage rise to kill it.
Ask any transformer expert what happens to a transformer designed with "graded insulation" (most single-bushing distribution transformers were made with it) when the line and grounded terminals are reversed.
** Graded insulation, accoring to my reference book, is windings with more insulation materials at the line end, and less insulation used/applied as the winding progresses to the grounded end. (Often the end closest to the core) This was done supposedly to save money, weight and give a very slight efficiency boost.
At the other end of this spectrum, the film projectors at a screening room I run are designed for 208-240 volts line-to-neutral, yet are running quite nicely (after 11 years) running 208 line-to-line. (The machines are German). Studying the schematic very carefully, there are NO components in it where HV and LV share any common reference. I think in the case of my platters and this vac, that common reference between HV and LV is the key issue to the problem.