Not sure which part of NEC ever mentions it, but if the service line is to be replaced, does the power panel have to be replaced too? If not, why is it required to have AFCIs to replace the current ones?
..AFCI are not required to be replaced unless there is work down on the circuit such as adding a new receptacle or switch..
Insurance adjusters, inspectors, and EC's may look more closely at renovation re-work than others.
Missing Tamper Resistant plugs after remodels is the 1st clue the place is riddled with code violations, not just missing AFCI's in the fuse box, or reset buttons, per replacement code 406.4(D)..
The rocket-scientist re-modelers give themselves away by grabbing the cheapest plugs stocked on store shelves.
The wrong plug violates fire code, voids insurance claims, and renders owner's powerless to negotiate favorable settlements with adjusters.
210.12(D) Branch Circuit Extensions or Modifications — DwellingUnits and Dormitory Units.
In any of the areas specified in 210.12(A) or (B), where branch-circuit wiring is modified,
replaced, or extended, the branch circuit shall be protected by one of the following:
(1) A listed combination-type AFCI located at the origin of
the branch circuit
(2) A listed outlet branch-circuit-type AFCI located at the first
receptacle outlet of the existing branch circuit
Exception: AFCI protection shall not be required where the extension of
the existing conductors is not more than 1.8 m (6 ft) and does not
include any additional outlets or devices.
Not sure which part of NEC ever mentions it, but if the service line is to be replaced, does the power panel have to be replaced too? If not, why is it required to have AFCIs to replace the current ones?
Not sure which part of NEC ever mentions it, but if the service line is to be replaced, does the power panel have to be replaced too?
Is/was this an old 60 amp service that needed new conductors? Yes, I can see a new 100. AFCIs,no. Smokes, yes but not an NEC requirement.
I live and work here. Your jurisdiction may have other rules, but respectfully ask for code references.
Okay, I start to get it.
So, local codes or state law requires smoke upon any permit work, (which is true because I have encountered more than twice) and then that installation could trigger AFCI. But shouldn't it be limited to the new circuit for the smoke, not the whole house?
I am really unhappy about these kinds of loop (local code requires something which triggers much more codes). Yes, I should ask for code reference. Just the same as why he asked for a new plug to be installed with 25' of the AC condenser together this service line job. I am not touching the AC at all! Even if the code now requires a receptacle, the AC was installed almost 20 years ago, when there was no such a requirement.
BTW, regarding to the receptacle requirement, can the outlet for the coil count (if the coil and the receptacle are with 25' of the condenser, though the receptacle and the coil are inside the house, but they are all on the same level).