I'm putting out a budget bid on a Multifamily Residential project in Broward County; the drawings are preliminary Architectural only, they are classified as R2 Residential apartment in Type IIIB buildings that are 4-stories. Is the use of Romex allowed in the construction of these units?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
334.10 Uses Permitted. Type NM, Type NMC, and Type
NMS cables shall be permitted to be used in the following,except as prohibited in 334.12:
(1) One- and two-family dwellings and their attached or detached garages, and their storage buildings.
(2) Multi-family dwellings permitted to be of Types III, IV,and V construction.
(3) Other structures permitted to be of Types III, IV, and V construction. Cables shall be concealed within walls,
floors, or ceilings that provide a thermal barrier of materialthat has at least a 15-minute finish rating as identified
in listings of fire-rated assemblies.
 