Hi,
We have designed a 5MW solar system and connected it to the MV utility pole. The solar system only generates power to the grid without supporting any load. The new solar system also has a disconnect switch (GOAB) to disconnect our solar system from the grid. Is the GOAB switch considered the service disconnect and required to follow section 230?
The NEC definition of "service" is "The conductors and equipment connecting the serving utility to the wiring system of the premises served." Is the solar system considered the "premises served"?
I believe the solar system only needs to follow section 690 and does not need to comply with section 230, but I want to know your opinion. We have been asked by the AHJ a few times to add the "service disconnect" label to the GOAB switch as required by section 230.70(B).
Thank you
We have designed a 5MW solar system and connected it to the MV utility pole. The solar system only generates power to the grid without supporting any load. The new solar system also has a disconnect switch (GOAB) to disconnect our solar system from the grid. Is the GOAB switch considered the service disconnect and required to follow section 230?