Does the NEC require conduits to be secured to the ground before rock is installed on top or concrete slab is poured. Also is there any requirement for spacing conduit apart per the NEC?
The inspector in our area is requiring PVC conduits to be secure to the ground by staking and requiring spacing between the conduits. The PVC conduits are installed on top of compacted rock and another 6" of (minus) rock will be installed on top of the conduits before the floor slab is poured. All the PVC conduits are 1" or 3/4".
Does 2008 & 2011 NEC article 352.30 apply to under slab conduits?
Thanks
The inspector in our area is requiring PVC conduits to be secure to the ground by staking and requiring spacing between the conduits. The PVC conduits are installed on top of compacted rock and another 6" of (minus) rock will be installed on top of the conduits before the floor slab is poured. All the PVC conduits are 1" or 3/4".
Does 2008 & 2011 NEC article 352.30 apply to under slab conduits?