Hi,
I am confused little or lot here,
installing 400A, 3ph-commertial service
series rating with 10 feet away mounted new sub panel that are same manuf. as the 400A service. which is "Siemens"
I am choosing series rating instead of fully-rating
hoping to save some money.
note that; local Utility fault report indicates 42000A avail. short cir. value
here is my design;
The main breaker in 400A service: "JD6-A" @ 65000AIC (,
The 200A-3p Breakers in 400A service: "QJ2H" @ 42000AIC'
The 20A-1P breakers in sub panels: "QPH" OR "BQH" @ 42000A
QUESTION IS,
Can i use the sub breakers (QJ2H , QPH, BQH) @ 10,000 AIC ????????
Tanx
I am confused little or lot here,
installing 400A, 3ph-commertial service
series rating with 10 feet away mounted new sub panel that are same manuf. as the 400A service. which is "Siemens"
I am choosing series rating instead of fully-rating
hoping to save some money.
note that; local Utility fault report indicates 42000A avail. short cir. value
here is my design;
The main breaker in 400A service: "JD6-A" @ 65000AIC (,
The 200A-3p Breakers in 400A service: "QJ2H" @ 42000AIC'
The 20A-1P breakers in sub panels: "QPH" OR "BQH" @ 42000A
QUESTION IS,
Can i use the sub breakers (QJ2H , QPH, BQH) @ 10,000 AIC ????????