looked at a job today - commercial building - power comes into building that goes to one main meter that then goes to a 225amp 3 phase 120-208v panel.
The last electrician then used 12/3 NM cable which was on a 2 pole 20amp breaker in that panel to feed another meter socket (did this 4 times - all right next to each other). then coming out of each meter was a tiny sub panel with 2 20amp 120v breakers in it feeding a small space -lights and receptacles. (there are 4 rooms - so 4 sub panels)
Essentially they are sub metering the 4 sub panels. Owner says he bought the (sub) meters online - they look like real regular meters. He reads them every month and does the math to subtract from the main meter or main bill and then bills each tenant for electricity use.
I have never seen this before and he said it was never inspected because the last electrician wasn't sure it was legal.
What he wants me to do is redo it with larger wire and 50amp 2 pole breakers so they can add electric heat to the spaces. (re use the existing meter sockets, replace the sub panels with larger ones and replace the sub panel wire feeds.
Any comments if this is a legal installation?
it works fine now but - I've never seen this done before - I intend on doing it the legal way with a permit but I want to do it correctly. The supply house told me to scrap it all and install this http://www.emon.com/products_class4000.htm#
anyone?
The last electrician then used 12/3 NM cable which was on a 2 pole 20amp breaker in that panel to feed another meter socket (did this 4 times - all right next to each other). then coming out of each meter was a tiny sub panel with 2 20amp 120v breakers in it feeding a small space -lights and receptacles. (there are 4 rooms - so 4 sub panels)
Essentially they are sub metering the 4 sub panels. Owner says he bought the (sub) meters online - they look like real regular meters. He reads them every month and does the math to subtract from the main meter or main bill and then bills each tenant for electricity use.
I have never seen this before and he said it was never inspected because the last electrician wasn't sure it was legal.
What he wants me to do is redo it with larger wire and 50amp 2 pole breakers so they can add electric heat to the spaces. (re use the existing meter sockets, replace the sub panels with larger ones and replace the sub panel wire feeds.
Any comments if this is a legal installation?
it works fine now but - I've never seen this done before - I intend on doing it the legal way with a permit but I want to do it correctly. The supply house told me to scrap it all and install this http://www.emon.com/products_class4000.htm#
anyone?