Is the front of a transformer considered exposed live part?

Status
Not open for further replies.
I don't believe you have to consider that transformer as something that would normally be energized when it's being worked on.
 
I have always used the enclosure cover to measure for clearances.

I don't think the intent is to measure from the live parts for the working clearances.

That could result in a significant reduction with a deep enclosure.
 
DHkorn said:
I don't believe you have to consider that transformer as something that would normally be energized when it's being worked on.


How do you check for phasing and voltage if the xformer is de-energized?
 
Last edited:
Im assuming your talking about a dry-type transformer under 600v.

Your answer lies in 110.26. Specifically 110.26(A)(1). 110.16 is also important.

The key phrase in this section is "examination, adjustment, servicing, or maintenance while energized".

All new transformers I have run across are labled with something like, " de-energize before working on " The manufacture is telling you not to examine, adjust, service, or maintane while energized. This being the case 110.26 would not apply to transformers of this type.

If you are talking about transformers over 600v the rules change, and I am not experienced enough to give a good answer about working space as it applies to transformers over 600v.

hope I was some help

ibew441dc
 