Is the main disconnect adequate?

Status
Not open for further replies.

Cmdr_Suds

Member
Does opening of the main disconnect in a control panel suffice in allowing a person to service a control panel without PPE even though there is still power at the top of the disconnect or breaker?

I have been seeing a second disconnect located nest to the panel so there is no power inside the control panel.

Any thoughts?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Does opening of the main disconnect in a control panel suffice in allowing a person to service a control panel without PPE even though there is still power at the top of the disconnect or breaker?

I have been seeing a second disconnect located nest to the panel so there is no power inside the control panel.

Any thoughts?
Technically, the line terminals are still hot and present a risk of exposure to arc flash energy, requipring the appropriate PPE for the amount of energy involved.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
If the supply side of the main disconnect is shielded, placed in a separate closed compartment, etc. it possibly could be deemed safe, but I think many have gone with external main disconnect to help avoid any confusion with this.
 