Is the physical size of the taps used counted somehow for wire capacity?
GerryB
I am adding a house meter to an existing 3-family house and meter set up. Ridgid conduit comes into a horizontal 3 gang meter bank in the basement. There is about an 8x10 cover where the three 3/0 copper lines come in and connect to the bus and feed the existing meters. I mounted my meter from a KO at the end where the conductors enter this meter provision. Since it is a house meter we are allowed to run as small as 30amp, I ran #6thhn.
The POCO looked at what I plan to do and approved it. I am a little concerned if the EI will have any issues. When I pulled the permit he said make sure there is enough room in the trough for the taps, but I think he was envisioning the set up where there is a trough with multiple taps to each meter. Those can get pretty crowded.
So I plan to tap the three 3/0 and the 3 #6 with insulation piercing Kup L Taps. They are about 2/5 " square. (The POCO uses them also). So if any one gets what I'm trying to do this access point has the three 3/0 come in the top and 90 into the meter lugs. That is all that is in there and it is the depth of a standard meter socket. I plan to stagger the taps.
I think I'm fine, someone could comment otherwise, my basic question was do you calculate the tap size for box fill requirements.
kwired
Electron manager
NE Nebraska
Measuring the tap devices can be a little tricky with odd shaped ones, but the rule is you can not exceed 75% of the cross section at any point of the wireway or aux gutter with conductors and other components. Staggering splices is a way to comply with this rule. Things get pretty crowded before you ever reach 75% so unless you are having trouble stuffing everything into the wireway, you have a good chance of being compliant.
GerryB
Great, thanks a lot.