It is basically a non contact voltage sensor coupled to the main wires. Since it is measuring through the normal insulation you don't need to worry about making an electrical connection before the main.

I installed one, not difficult at all. Don't recall how loud it was, don't recall its battery requirements.

Jon
 
It is basically a non contact voltage sensor coupled to the main wires. Since it is measuring through the normal insulation you don't need to worry about making an electrical connection before the main.

I installed one, not difficult at all. Don't recall how loud it was, don't recall its battery requirements.

Jon
Have you used it since it was installed?
 
The unit was used once since installed.

It has a switch on the side; you have to turn it on when switching over to the generator. It will then sound when mains comes back on.

The location was in the far corner basement of a wood framed somewhat sprawling structure. It could be heard over half of the first floor.

(Reports from the friends using it, not direct experience.)

-Jon
 
That's a skookum little unit for under $50... Too bad it doesn't have a relay output that you could wire to something else, but being powered from a 9V battery, I can see why.
 
Relay powered by utility side of transfer switch. Make it operate a "kill switch" for the generator when utility is active, put a delay on it if you want to prove utility for certain time period first, override switch in the kill circuit if you want to run generator for any reason when utility is active.

Loss of generator power will get owner/occupant attention and you can have a visual indicator of some sort at transfer switch or generator to indicate utility is on.
 
Relay powered by utility side of transfer switch. Make it operate a "kill switch" for the generator when utility is active, put a delay on it if you want to prove utility for certain time period first, override switch in the kill circuit if you want to run generator for any reason when utility is active.

Loss of generator power will get owner/occupant attention and you can have a visual indicator of some sort at transfer switch or generator to indicate utility is on.
Isn’t that what the green light on automatic transfer switches do now?.😅
 