Per NFPA 2016 18.4.5.3, the audible appliances in sleeping areas shall be the low frequency type. We are now required a low frequency sounder or sounder strobe in sleeping/dwelling units to notify the fire alarm signal of the building fire alarm system. Are the smoke alarm in side and outside the bedrooms in a dwelling units, or sleeping area in hotel etc. required to be low frequency type? I am not talking about the smoke alarm instead of smoke detector that is connect to the fire alarm system.
However I can't find a manufacture that has low frequency smoke or smoke/co alarm. Do you guys know any manufacture that has low frequency smoke or smoke/co alarm.
Another option is to install smoke detector with low frequency sounder base in sleeping/dwelling units and connected to building fire alarm system. But configure those smoke detectors to activate only the sounder base in the unit rather than the building fire alarm system. But this will cost much more than smoke alarms. One smoke alarm is only $30-$50 bucks I guess. You will also need extra cost for programing and wiring. Besides, when I look into the products from silent knight, I think the smoke detector with sounder base only work in addressable fire alarm system. In this option, you will need addressable fire alarm system for 3-4 units multifamily.
However I can't find a manufacture that has low frequency smoke or smoke/co alarm. Do you guys know any manufacture that has low frequency smoke or smoke/co alarm.
Another option is to install smoke detector with low frequency sounder base in sleeping/dwelling units and connected to building fire alarm system. But configure those smoke detectors to activate only the sounder base in the unit rather than the building fire alarm system. But this will cost much more than smoke alarms. One smoke alarm is only $30-$50 bucks I guess. You will also need extra cost for programing and wiring. Besides, when I look into the products from silent knight, I think the smoke detector with sounder base only work in addressable fire alarm system. In this option, you will need addressable fire alarm system for 3-4 units multifamily.