Is there a code that requires a Polyphaser to be (1) Outside and (2) in a Box?

Status
Not open for further replies.

Installer

Senior Member
I've been seeing them this way for many years now.
We take our Antenna cables for our Radios, and feed them through a Polyphaser in a NEMA3 or NEMA4 enclosure outside,
with the Bus Bar attached to a 4/0 down comer before we send them into the Equipment Room in the Building.
Is their a Code or Requirement that states this, or is it a Trade Practice?
Can a Polyphaser be mounted on a Bus Bar inside a Building?
Personally I don't see why not, but if I do it, I'm sure I'll be criticized and asked to redo it.

20210622_144237.jpg
 

tom baker

First Chief Moderator
Staff member
It would help if you e explain what a polyphaser is...I have installed around 75. Mine went just inside the building, on a ground bar, with the bonding jumper going back oudfe to the building GES. As far as cofe, what fo the instuctions say as far as being outside.
 