Is there a difference between 400/100 and 400:1.73/100:1.73 transformers??
Kaaud
Is there a difference between 400/100 and 400:1.73/100:1.73 voltage transformers
My guess is the ratio is the same , but one is wye/wye and the other is delta/delta. Am I correct or there is no difference??
I, for one, don't recognize those ratios as transformer designations. I could make educated guesses, but, can you tell us more about them? Actual voltage ratings and winding configurations?
IEC voltage transformers may have a line-neutral rating listed as (Volts phase-phase)/ (sqroot 3). Instead of a 277V winding it would be listed as 480/ Sqroot3 or 480/1.73.
The two ratios you listed are the same.
In the ANSI world VT's are often supplied with a 120V/69.3V secondary to feed protective relays or meters. The 120V tap is for devices that need 120V phase-to-neutral. The 69.3 volt tap is for devices that need 120V phase-phase. The 100/1.73 rating would be for supplying the IEC standard secondary voltage of 100V phase to phase in a wye connected VT bank.