I got dragged into this situation where a landlord was trying to replace meter cans on his 4-apartment house, and the city and inspector won't let him only replace the meter cans because the 4 individual services were originally only 40 amps each, and he wants to stay with that. Of course, I know that dwelling units now require minimum 100A service, but it doesn't make a lot of sense for these particular units. All appliances are gas and they want to keep it that way.
To avoid having to run all new service wires and put 4 new panels, I suggested bringing it all under one service, and splitting off 4 feeders to the apartments. When doing it that way, if the load calculation comes up OK, would it be prohibited by code to re-use the existing 40-amp services, but make them (4) 40-amp feeders instead? It seems small for an apartment feeder, but these are small apartments without laundry facilities and I don't know if there is some minimum size require by code.
I know that equipment grounding conductors would likely have to be added and grounds separated from neutrals in the existing main panels which would become sub-panels.
I'm going to do a load calculation today and see how it comes out.
To avoid having to run all new service wires and put 4 new panels, I suggested bringing it all under one service, and splitting off 4 feeders to the apartments. When doing it that way, if the load calculation comes up OK, would it be prohibited by code to re-use the existing 40-amp services, but make them (4) 40-amp feeders instead? It seems small for an apartment feeder, but these are small apartments without laundry facilities and I don't know if there is some minimum size require by code.
I know that equipment grounding conductors would likely have to be added and grounds separated from neutrals in the existing main panels which would become sub-panels.
I'm going to do a load calculation today and see how it comes out.