is there a requirment to remove 20% load from the main panel

Status
Not open for further replies.

fittowork11

Member
Location
hayward ca
Occupation
contractor
Hi Everyone

I have caluculate my load factors for a 3 unit building at 184 amps, My question is according to The Nec can I use a 200 amp service or do I need to remove 20% off of the 200 amps to get 160 amps that would be intern to small (please if someone can exsplain how this works)

Thanks

Brian
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Welcome to the forum.

You need to provide more info. Is this a residential building or non residential. Is the 184 amps continuous?

Please share your calculations.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the load calculation is according to Article 220 the calculated load is used to size the service. If you calculation comes up with 200 amps then that is your minimum service size. You do not need to do anything to the calculated load.
 

fittowork11

Member
Location
hayward ca
Occupation
contractor
If the load calculation is according to Article 220 the calculated load is used to size the service. If you calculation comes up with 200 amps then that is your minimum service size. You do not need to do anything to the calculated load.
This is what I got according to artical 220 (at the moment the main house panel is suplied by a 250 mcm THW (Aluminum)


Calculated load Unit 1 970 sqft Unit2 970 sqft Unit3 580 sqft Total
General lighting 970 x 3va =2910 970 x 3va = 2910 580 x 3va = 1740 7560 VA
Small appliance 3000 va 3000 va 3000 va 9000 VA
dishwasher 1200 va 1200 va 2400 VA
Laundry circuit 1500 va 1500 va 3000 va
disposal 760 va 760 va 1520 va
Stove hood 300 300 va 600 va
Fridge (is this needed) 600 va 600 va 600 va 1800 va
Total 25880/120= 216 amps
 

RWC/NC.

Senior Member
Location
N.Carolina
Occupation
Electrical
Noticing laundry circuit unit(s) one & three. Curious are there no electric clothes dryers, in the two separate units. Also noticing range hoods, might dwelling ranges & hot water heaters along w/unit heating equipment be gas, in lieu of electric. Are there any AC loads being considered (?)
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
This is what I got according to artical 220 (at the moment the main house panel is suplied by a 250 mcm THW (Aluminum)


Calculated loadUnit 1 970 sqftUnit2 970 sqftUnit3 580 sqftTotal
General lighting970 x 3va =2910970 x 3va = 2910580 x 3va = 17407560 VA
Small appliance3000 va3000 va3000 va9000 VA
dishwasher1200 va1200 va2400 VA
Laundry circuit1500 va1500 va3000 va
disposal760 va760 va1520 va
Stove hood300300 va600 va
Fridge (is this needed)600 va600 va600 va1800 va
Total25880/120= 216 amps
You divide by 240, not 120
25880/240=107.83A
 

kwired

Electron manager
Location
NE Nebraska
You divide by 240, not 120
25880/240=107.83A
or 208 and square root of three if that applies, but either way makes a significant difference from using 120. May or may not be other demand factors available not mentioned in his spreadsheet, and as mentioned probably is also heating or cooling load that isn't in the sheet, would only need to consider whichever is larger load.
 

fittowork11

Member
Location
hayward ca
Occupation
contractor
or 208 and square root of three if that applies, but either way makes a significant difference from using 120. May or may not be other demand factors available not mentioned in his spreadsheet, and as mentioned probably is also heating or cooling load that isn't in the sheet, would only need to consider whichever is larger load.
Hi Kwired

yes you are right I definatly made a mistake with dividing by 120

Thanks makes the service mutch small LOL
 

fittowork11

Member
Location
hayward ca
Occupation
contractor
Bill, it appears possibilities he's also missed utilizing Table 220.42 lighting load demand factors.
Hi I was under the impression from the nec that multi unit building that are not apartments are treated as individule residence when using demand factors or am I wrong Thanks for your advice
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Hi I was under the impression from the nec that multi unit building that are not apartments are treated as individule residence when using demand factors or am I wrong Thanks for your advice
If the calculation method you used was the optional see table 220.84 also. Keep in mind you likely have a 4th panel needed for loads in common areas. You may want to look at annex D example D4(b)
 

kwired

Electron manager
Location
NE Nebraska
Hi I was under the impression from the nec that multi unit building that are not apartments are treated as individule residence when using demand factors or am I wrong Thanks for your advice
There not many categories in the table. Dwelling units, hospitals, hotel/motels and warehouses. You apply whatever demand factor applies to each category if present and 100% for all other situations.

Even in a multifamily dwelling situation you likely have "house loads" that are taken at 100% where the rest of the calculations can take advantage of dwelling unit demand factors.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
Multi family, service calc.
Take it the stove is gas. You mentioned hood for stove.
Gas dryer maybe?
no HVAC ?
There is some examples in the back of the book to help guide you. Informative Annex D Examples.
I use them a lot.
edit
Sorry dm9289 did not see you already stated annex D.
 