Is there an instance where you wouldn't have to derate?

Status
Not open for further replies.

Jonathan23

Member
Location
Beaumont
Occupation
Electrical Engineer
I was wondering if there is an instance where a run of conduit is short enough that you would not have to worry about derating the conductors inside the conduit? Is there a section in the code that would give me this answer? Any help will be helpful.
 

HEYDOG

Senior Member
I was wondering if there is an instance where a run of conduit is short enough that you would not have to worry about derating the conductors inside the conduit? Is there a section in the code that would give me this answer? Any help will be helpful.
310.15(c)(1)(b)
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
I was wondering if there is an instance where a run of conduit is short enough that you would not have to worry about derating the conductors inside the conduit? Is there a section in the code that would give me this answer? Any help will be helpful.
24” and less
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I was wondering if there is an instance where a run of conduit is short enough that you would not have to worry about derating the conductors inside the conduit? Is there a section in the code that would give me this answer? Any help will be helpful.


I don't know if you are aware of this but you can de-rate from the 90C column as long as the load is not greater than the 75C column (assuming you have 90C wires)
 
Status
Not open for further replies.
Top