is there any code restriction regarding max branch circuit per panel and unbalance percentage between phases?
I am not entirely sure what you are asking but there are no restrictions on the quantity of branch circuits in a panel, nor on how unbalanced they are. Those are strictly design considerations.
However, you still have to abide by whatever calculated load you came up with for each branch circuit, and then for the feeder circuit(s).
as standard practice, we ask for 5% max unbalance between phases. any code reference for that or it is just a common /design practice?
on the other hand i think its manufacturer recommendation about max over current devices per panel
as standard practice, we ask for 5% max unbalance between phases. any code reference for that or it is just a common /design practice?