A fully protected conductor feeds a control panel to a disconnect switch.
A tap on the line side of the disconnect switch provides power to a lighting transformer.
My contention is that this is a feeder tap IAW 240.21 and thus as long as it is less than 10 feet long and does not leave the enclosure that it can be any size that is protected at its ampacity downstream.
A customer is claiming the ampacity of the such a tap must be at least 10% of the OCPD feeding it. The rule seems quite clear to me. But, maybe I am missing something.
Incidentally, in rereading this section, there seems to be a gray area in it. If the tap is longer than 10 feet even if it does not leave the box it appears it would not qualify under this section and would have to meet one of the other tap rules. Am I reading ti correctly?
Just curious, what rules are there for branch circuit taps? There don't appear to be any similar provisions.
A tap on the line side of the disconnect switch provides power to a lighting transformer.
My contention is that this is a feeder tap IAW 240.21 and thus as long as it is less than 10 feet long and does not leave the enclosure that it can be any size that is protected at its ampacity downstream.
A customer is claiming the ampacity of the such a tap must be at least 10% of the OCPD feeding it. The rule seems quite clear to me. But, maybe I am missing something.
Incidentally, in rereading this section, there seems to be a gray area in it. If the tap is longer than 10 feet even if it does not leave the box it appears it would not qualify under this section and would have to meet one of the other tap rules. Am I reading ti correctly?
Just curious, what rules are there for branch circuit taps? There don't appear to be any similar provisions.