is this a legal emergency lock-out mechanism?

Status
Not open for further replies.

malachi constant

Senior Member
Location
Minneapolis
HI all,
I've never seen this before. It appears to be a mechanical device for a manual emergency power transfer system that prevents the utility and generator breakers from being simultaneously closed. We found one instance where the transfer protocol was clearly labeled, but this particular building there was minimal labeling. Is it legal?
 

Attachments

  • 090620.jpg
    090620.jpg
    135.1 KB · Views: 0
Looks good to me. Not one of those internet brands but from an actual OEM lockout kit.
 
Does anyone have a requirement that states that these interlocks have to be listed?
 
Discussion limited to Optional Standby Systems

I agree, they work great and are safe.
Does anyone have a requirement that states that these interlocks have to be listed?

Yes sometimes that is an issue but it should not be.

NEC 702
No mention of transfer switches requiring listing
Recognizes gens less than 15kW may be un-bonded​

NEC 445 Recognizes gens less than 15kW may be un-bonded

NEC 250.34, 250.35

For this type of interlock, the gen is not a Separately Derived System. The house and generator neutrals are solidly connected. One would have to remove the N-G bond in the generator.

It is what I used I my last house.

Well, there is one safety issue. There are inspectors that will burst into flames walking by the installation.

the worm
 