Hello,
Im trying to hook up power to my new office trailer, from a subpanel of a nearby shed. The office has 120V ligthing and receptacles, and a 240V A/C unit. The subpanel that I intend to use for the source is a 60A 415Y/240V 3-phase panel.
It would probably be easiest to just get a ~25kva 240V to 240V-120V transformer and run the 240-120 split-phase panel on the office trailer as it is intended. Im trying to avoid this becasue I would like to reuse a cheap 5kva 240V to 120V single phase transformer I already have. The goal is to run the lighting and AC off the 5kva transformer while feeding the A/C unit directly with my already existing 240V at the subpanel. I am also adding an extra 240V receptacle at the office.
I attached a layout of how I think this can work, but have concerns regarding the grounding and whether half of what I am doing is even allowed.
To assist with the diagram, i will explain below...
1. Install 3x 30A breakers in the sub panel.
2. Run 3x lines of hot 10awg, 3x 10awg nuetrals, and a 10awg ground to the transformer in a single 3/4" conduit.
3. Pass circuits from P1 and P2 through the transformer to the office panel, no connections.
4. Connect P3 circuit to 5kva across H1/H3 and H2/H4 accordingly to get 120V on the secondary accross X4 and X1 (X2 and X3 connected). Tie ground to the transformer chassis.
5. Feed 120V into office panel along with the other 2x 240V circuits, single conduit.
6. Inside office panel, bond X1 (identified as the nuetral) from transformer to ground/nuetral bus. My understanding is this should be bonded despite being a sub panel since the 120 circuit is isolated. Drive a ground rod and connect to bus as well.
7. With a ground ran between the ground/nuetral bar to each 240V circuit, one can connect to the existing AC wiring, the other circuit can go to the newly installed 240V receptacle on the exterior of the bulding.
8. The 120V line will feed the already existing panel through a 30A breaker, the light and receptacles will be ran off 2x 30A breakers already inside the panel. They appear to share a nuetral (as the office came), and are accordingly on a shared double 30A breaker. Ground connected to the ground/nuetral.
So this might seem like a stupid, and possibly horrible, way to do this. Might be fun to pick apart and tell me I have no business doing this.
Thanks!
Im trying to hook up power to my new office trailer, from a subpanel of a nearby shed. The office has 120V ligthing and receptacles, and a 240V A/C unit. The subpanel that I intend to use for the source is a 60A 415Y/240V 3-phase panel.
It would probably be easiest to just get a ~25kva 240V to 240V-120V transformer and run the 240-120 split-phase panel on the office trailer as it is intended. Im trying to avoid this becasue I would like to reuse a cheap 5kva 240V to 120V single phase transformer I already have. The goal is to run the lighting and AC off the 5kva transformer while feeding the A/C unit directly with my already existing 240V at the subpanel. I am also adding an extra 240V receptacle at the office.
I attached a layout of how I think this can work, but have concerns regarding the grounding and whether half of what I am doing is even allowed.
To assist with the diagram, i will explain below...
1. Install 3x 30A breakers in the sub panel.
2. Run 3x lines of hot 10awg, 3x 10awg nuetrals, and a 10awg ground to the transformer in a single 3/4" conduit.
3. Pass circuits from P1 and P2 through the transformer to the office panel, no connections.
4. Connect P3 circuit to 5kva across H1/H3 and H2/H4 accordingly to get 120V on the secondary accross X4 and X1 (X2 and X3 connected). Tie ground to the transformer chassis.
5. Feed 120V into office panel along with the other 2x 240V circuits, single conduit.
6. Inside office panel, bond X1 (identified as the nuetral) from transformer to ground/nuetral bus. My understanding is this should be bonded despite being a sub panel since the 120 circuit is isolated. Drive a ground rod and connect to bus as well.
7. With a ground ran between the ground/nuetral bar to each 240V circuit, one can connect to the existing AC wiring, the other circuit can go to the newly installed 240V receptacle on the exterior of the bulding.
8. The 120V line will feed the already existing panel through a 30A breaker, the light and receptacles will be ran off 2x 30A breakers already inside the panel. They appear to share a nuetral (as the office came), and are accordingly on a shared double 30A breaker. Ground connected to the ground/nuetral.
So this might seem like a stupid, and possibly horrible, way to do this. Might be fun to pick apart and tell me I have no business doing this.
Thanks!