Senior Member
- Location
- Pennsylvania
A friend with 30 + years inspecting asked what I thought about a conflict he was having. The contractor took a feeder from an 800- amp service 150 amp breaker to a sub panel with a main breaker. The panel also has feed through lugs off the 150- amp bus.
The feed from the 800- amp service went to the feed trough lugs not the 150 amp main. From the 150 amp main breaker another feeder was taken to feed another sub-panel for some pump equipment.
The senior inspector told the contractor he would not pass this installation stating if someone was to turn off the main this panel would still be energized and some one is going to get hurt thinking they killed the main. The contractor argued that a sub panel did not need a main. The senior inspector stated he is not disputing the fact that the sub panel did not need a main but rather since this panel has a main he would not pass the feeder to this panel being tied into the main lugs.
The contractor went over the inspector?s head and took his argument to the owner of the inspection agency. The owner said to pass the installation. The inspector refused stating it his name on the sticker and he does not believe this to be safe.
The feed from the 800- amp service went to the feed trough lugs not the 150 amp main. From the 150 amp main breaker another feeder was taken to feed another sub-panel for some pump equipment.
The senior inspector told the contractor he would not pass this installation stating if someone was to turn off the main this panel would still be energized and some one is going to get hurt thinking they killed the main. The contractor argued that a sub panel did not need a main. The senior inspector stated he is not disputing the fact that the sub panel did not need a main but rather since this panel has a main he would not pass the feeder to this panel being tied into the main lugs.
The contractor went over the inspector?s head and took his argument to the owner of the inspection agency. The owner said to pass the installation. The inspector refused stating it his name on the sticker and he does not believe this to be safe.