What dictates the size of the bonding jumper required for Rigid Metal Conduit stubups if there are multiple involved?


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are you referring to a feeder? If so each bonding jumper is sized according to T250.122 and the OCPD size.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Are you referring to a feeder? If so each bonding jumper is sized according to T250.122 and the OCPD size.

What if you have several feeders being stubbed up in several rigid metal conduits? Could you bond them all together based on the largest feeder?