Is this Class 1 Div 2 Guideline up to code or am I missing any crucial parts?

Status
Not open for further replies.

DownRiverGUy

Member
Location
Canton, MI
I am writing out a brief guideline for electrical practices in a warehouse area that is Class 1 Div 2. I just wanted to make sure I'm not missing any area. The goal is to not overbuild this place and have Class 1 Div 1 practices where Class1 Div 2 would be fine.

Let me know if any further information is needed and/or if this guideline seems up to snuff with you guys.

As always thanks for posting :smile:

THIS SPEC CLARIFIES NEC 2005 PRACTICES ON CLASS 1 DIVISION 2 AREAS. ANYTHING NOT COVERED IN THIS SPEC SHALL AT THE MINIMUM COMPLY WITH THE 2005 NEC.

Light Switches: Must be in an explosion proof enclosure and sealed according to 501.15B and E. Wiring methods must comply with 501.10B.

Light Fixtures: If rated for Class 1 Div 2 can be wired with standard jboxes etc so long as the wiring method complies with 501.10B and E.

*Regarding 501.10B4 in the blue comment section they mention "lighting outlets" what exactly does that mean? Is it an outlet labeled specifically for only lighting applications?*

Receptacles: Must be Class 1 Div 2 and sealed according to 501.15B and E. Wiring methods must comply with 501.10B.

Fire Alarm Strobes, Pulls, Horns, and Audible Strobes: If rated for Class 1 Div 2 can be wired according to 501.10B. However if they are not they must be Class 1 Div 1 rated and be enclosed in explosion proof boxes and sealed according to 501.15B and E. Wiring methods must comply with 501.10B.

Additional Seal Locations: Immediately after leaving the Class 1 Division 2 location all conduits must be sealed according to 501.15B prior to any other conduit separation.
 
Check NFPA 30. Storage in warehouse areas without dispensing or open containers is unclassified.
The next to the last line in Table 515.3 says the same thing. In fact, the whole Table is extracted from NFPA 30, Table 8.2.2.

The real advantage of consulting NFPA 30 is determining whether you have a bulk storage facility at all. :grin:
 