Is this code

Kvbhcn

Member
Location
Virginia
Occupation
Electrician/hvac
I have a conduit ran direct across the opening of a junction box. Will this pass code. Looking for answers
 
I wish I new how to post a pic but part of the conduit is actually touching the cover of the box
 
It's ugly but code compliant because the EMT doesn't make the box inaccessible.
 
The cover can be removed and access to the wires is not a question so I believe this is compliant but I don't like it. hahaha
Agree with your comment, wonder if a offset could have worked to get around the box would work, without running afoul of the 360° max bends req.?
 
Top