Is this correct ?





I feel it's not. For one the neutral bond should be no smaller than the largest current carrying conductor As also the secondary should be grounded to XO It might be I'd have to look closer these were secretly taken as well as the 600 volt primary 150kva X former is way oversized for a 480/277 secondary. Am I right or just missing something ?
Eric






I feel it's not. For one the neutral bond should be no smaller than the largest current carrying conductor As also the secondary should be grounded to XO It might be I'd have to look closer these were secretly taken as well as the 600 volt primary 150kva X former is way oversized for a 480/277 secondary. Am I right or just missing something ?
Eric