WTR

Member
Location
Trxas
Occupation
P&C tech Utility
bf73c61039d3b08db6d761abcde15745.jpg

d61459a339c2c2a208c25f0f474b503c.jpg



Sent from my iPhone using Tapatalk
 
Not sure what I'm looking at exactly (panel mounted single phase outlets?) but my first thought is that it seems to be missing a bonding jumper to the frame of the equipment to which to EGC would be connected, which to ptonsparky's point would mean a nasty shock if one of those hot conductors shorts to the metal plane you're holding.
 
It's a piece of equipment so the NEC is meaningless.
"correct" or "incorrect" would depend on the standard that applied.
Do you know if it is NRTL Listed ??
 
Those appear to be factory installed, so NEC is probably not applicable. But as others have said, it does not appear to have a bond jumper from the equipment to the panel. But that being said, if the panel is not hinged, a cover screw should be marked as ground, along with a star washer insuring a bonding path.
 
It's a piece of equipment so the NEC is meaningless.
"correct" or "incorrect" would depend on the standard that applied.
Do you know if it is NRTL Listed ??
I agree, looks like it's integral to a piece of listed equipment so the NEC does not apply.
 
So we're talking about the EGCs. Aren't the receptacles' EGCs tied to the yokes?

I agree that the panel should have a jumper to the enclosure.
 
I see nothing wrong with your hard hat on the floor mines there all the time. Or do you mean the device make up.
The one wire looks a little discolored. Maybe a loose connection there.
 
My bigger concern with the MWBC aspect is they using the devices to splice the neutral. As said this probably not subject to NEC, but if it were it would need a pigtail to each device instead of a jumper between devices. 4th device has separate neutral to it, but that would be outside the "MWBC" supplying the other three devices so makes sense there.
 
I was wondering about the ground and neutral jumping. This is a container being used for servers. The customer was wondering if it was up to code. All I know is that has a UIL sticker on the structure. Will try and find out more. Thank


Sent from my iPhone using Tapatalk
 
The row is being feed by 200amp three poor breaker. The plugs are ABCAB.


Sent from my iPhone using Tapatalk
 
49c6d291f6df5169efc1bf2fb2b3b397.jpg

Found this set up in the build/ container today.


Sent from my iPhone using Tapatalk
 
Again this likely part of something not covered by NEC, but if so continuity of EGC can not be interrupted by removal of a device.
 