Geoffrey Lyons
Member
Is this correct,practical,or not to code. I have three pcs of equip to move to another spot in shop at present fed from busway (three seperate drops) ITE, bull dog type , new spot is only about a 15 ft run away from GE spectra busway, no 30 amp buss plugs in house 1- 60 amp in house. ea piece equip 240 1 ph 15 amp, could I use 60 plug,fused at 60 # 6 thhn run to centralized box tap 3 runs to 3-30 amp fused disconnects ea fused at 20 -12 thhn that feed recepts for ea equip . 30 amp buss plugs are about $400.-$500. ea plus not always on shelf. Other alternative 80 ft away is panel then theres 3-2 pole breakers conduit run..... Just want to do whats right