Hello,
Pool man sent me to look at pool at a residence that hasn't been opened in 10 years.
Owner is thinking about opening it and selling house.
Power goes to a pool house or shed (mens room, ladies room center is equipment) .Looks to have been installed in 50's or 60's.
Looks like 3/4 rigid with 3 wire #12 uf sleeved feeding a federal panel. The panel has 12 or so circuits feeding the pool house, maybe outside lights and equipment..
two motors, gas heater.
(not getting too crazy in this, but looks like there's an fs box under the panel 3/4 rigid in and out of the bottom, 3/4 out of top to panel. The wires in one 3/4 in bottom of fs box goes through the top and seems to be feed to panel, the ground of that wire is insulated and goes right out through the other 3/4 entering the bottom of the fs box (no ground to panel). A hot and neutral come from the panel and into that 3/4 out of the bottom of the fs box that the ground runs.... I "think to a deck box which is located under the diving-bored)
Couple questions.. I am enclosing a picture of the deck box... is it right?
to the far right is rigid 3/4 that a solid #8 ground is coming into. it is bonded to the metal of the deck box.
The center looks like copper with a 3 wire sj or something (the light).
The left is pvc with the light circuit ( although at pool house it is rigid... there may have been work done?? the cement maybe looks different)
But I'm asking because, I'm confused about the bond... from reading and recent posts, the bond doesn't go to the deck box.... an insulated 8 goes from the box to the fixture along with the light ground. And the circuit ground goes to the box...
in and around this pool there are some metal ladders.. I can't tell if they are bonded. at the deck box diving board ,, there are two poured short small cement walls that the dive sits between. there are two pieces of metal between the walls that the board sits on and two metal railings out of the tops of the cement...
Would all of that need to be bonded?
There is a bond wire at the pumps and the one in and out at the deck box so I'm guessing it was done right at the time..
When did the equipotential grid come into existence ? I doubt it has one, but wouldn't know for a fact.
Is there any way to tell... guess the grid would need a visually, as far as the ladders and any metal or the pool, any measurements, or there too would be visual?
So looking at this mess I'm considering not even reusing or trying to reuse whats there.
I wasn't able to get into the house, but guess by guess is it's an older federal also,
My thought is to feed the pool house with a new conduit and feeder as if whatever electrical is there isn't..(not sure how the gas pipe feeding the old heater is so maybe a 100 or 150 amp feeder.)
Cement cut around pool for equipotential grid and pick up ladders and board...and light...
I should be ok with a panel there right...as long as the ground is insulated..the pool equipment can go to it.?
In reading I believe so, and there are conditions of bare ground for existing..
As not to waste time, guys probably just thinking or shopping numbers, but was considering the bond in and out at the deck box and what year the perimeter surface bond came to be..
thank you..
Pool man sent me to look at pool at a residence that hasn't been opened in 10 years.
Owner is thinking about opening it and selling house.
Power goes to a pool house or shed (mens room, ladies room center is equipment) .Looks to have been installed in 50's or 60's.
Looks like 3/4 rigid with 3 wire #12 uf sleeved feeding a federal panel. The panel has 12 or so circuits feeding the pool house, maybe outside lights and equipment..
two motors, gas heater.
(not getting too crazy in this, but looks like there's an fs box under the panel 3/4 rigid in and out of the bottom, 3/4 out of top to panel. The wires in one 3/4 in bottom of fs box goes through the top and seems to be feed to panel, the ground of that wire is insulated and goes right out through the other 3/4 entering the bottom of the fs box (no ground to panel). A hot and neutral come from the panel and into that 3/4 out of the bottom of the fs box that the ground runs.... I "think to a deck box which is located under the diving-bored)
Couple questions.. I am enclosing a picture of the deck box... is it right?
to the far right is rigid 3/4 that a solid #8 ground is coming into. it is bonded to the metal of the deck box.
The center looks like copper with a 3 wire sj or something (the light).
The left is pvc with the light circuit ( although at pool house it is rigid... there may have been work done?? the cement maybe looks different)
But I'm asking because, I'm confused about the bond... from reading and recent posts, the bond doesn't go to the deck box.... an insulated 8 goes from the box to the fixture along with the light ground. And the circuit ground goes to the box...
in and around this pool there are some metal ladders.. I can't tell if they are bonded. at the deck box diving board ,, there are two poured short small cement walls that the dive sits between. there are two pieces of metal between the walls that the board sits on and two metal railings out of the tops of the cement...
Would all of that need to be bonded?
There is a bond wire at the pumps and the one in and out at the deck box so I'm guessing it was done right at the time..
When did the equipotential grid come into existence ? I doubt it has one, but wouldn't know for a fact.
Is there any way to tell... guess the grid would need a visually, as far as the ladders and any metal or the pool, any measurements, or there too would be visual?
So looking at this mess I'm considering not even reusing or trying to reuse whats there.
I wasn't able to get into the house, but guess by guess is it's an older federal also,
My thought is to feed the pool house with a new conduit and feeder as if whatever electrical is there isn't..(not sure how the gas pipe feeding the old heater is so maybe a 100 or 150 amp feeder.)
Cement cut around pool for equipotential grid and pick up ladders and board...and light...
I should be ok with a panel there right...as long as the ground is insulated..the pool equipment can go to it.?
In reading I believe so, and there are conditions of bare ground for existing..
As not to waste time, guys probably just thinking or shopping numbers, but was considering the bond in and out at the deck box and what year the perimeter surface bond came to be..
thank you..