mbrooke
Batteries Included
- United States
- Technician
Yes and no. Per 250.66(A), if you are only connecting to rods, pipes, or plates, and there is not a different type of electrode further downstream, then #6 copper is sufficient. That is the "yes" part. The "no" part is that the grounding electrode conductors need to be attached to the neutral bus, not the equipment ground bus. I know that they are bonded together, but right is right nonetheless.
Thanks
But- help my understand why code says its ok:
1) The gas pipe is technically a grounding electrode as metal gas mains can run the entire town.
2) A 600amp circuit could energize the fire sprinkler pipping as much as a 200amp circuit.
The gas pipe should have a di-electric union that prevents the gas pipes from acting like a grounding electrode.
It's in NFPA13 and I believe somewhere in chapter 10 it specifically prohibits using Fire Sprinklers for GE'sWhat code section?
See 250.104(B)But that still does not take care of #2
Why does the code say that if you run a GEC to structural steel, you size it on the basis of the service conductor size, but if you run one to a ground rod, you need not go bigger than #6 no matter how large the service conductor are? I have no idea.But- help my understand why code says its ok:
2) A 600amp circuit could energize the fire sprinkler piping as much as a 200amp circuit.
A single (or even multiple) ground rod will not have an ultra low resistance even in the best soil, where as structural steal can be the equivalent of 10,000 ground rods in parallel. Also I would think structural steal could in theory become energized by the largest circuit in the building where as a ground rod is not likely.
Regarding item 1, I can't answer for K8MHZ's comment. It may be a plumbing code, but I don't think it is in the NEC. However, a water pipe can serve as an electrode if it has at least 10 feet in contact with dirt. How long it is after that, even if it runs all through the town, matters not in the least.
Regarding item 2, if any circuit comes into contact with a piping system that is serving as a grounding electrode, that electrode will utterly disregard the event. By that I mean that dirt will not become part of the fault-clearing path. Rather, the bonding conductors that essentially tie all metal throughout the building, metal that has the possibility of becoming energized, back to the main panel's grounding bus, and from there to the neutral bus via the main bonding jumper, will establish a low-impedance circuit. This will result in a high current that will terminate the event by tripping the main, feeder, or branch circuit breaker, depending on where the fault took place.
It appears to me that you are confusing the grounding electrode system with the fault clearing duties of the equipment grounding conductors and bonding conductors.
Of course, which is why you would want the gas, fire, ect bonding conductors sized to 250.122. Do you want a 600amp circuit being cleared via #6?
It just make no sense to me that structural steel and the water main need 3/0 but not the rest of the piping.
See 250.104(B)
Roger
I think not. Your citation is related to bonding jumpers. The original question, and the sketch, are related to grounding electrode conductors. See my code citation in post #2.As I'm reading it, #6 would be a code violation?
(B) Other Metal Piping. If installed in or attached to a building
or structure, a metal piping system(s), including gas piping,
that is likely to become energized shall be bonded to any of the
following:
(1) Equipment grounding conductor for the circuit that is
likely to energize the piping system
I agree with Roger, in that that is how to deal with the bonding jumpers. But I repeat that this thread is not about bonding jumpers. It is about GECs.
The way I read the diagram, the column of items on the right are items to be bonded, not electrodes. The rest of the items are grounding electrode system.
Yes, but to me a gas pipe needs a grounding electrode conductor, not a bonding jumper. I guess the question is what guarantee is there that the gas pipe will have an isolating union.
The gas pipe cannot be a grounding electrode as mentioned above and often times there is a dielectric fitting between the gas meter and the interior pipes... Of course depending on where the meter is located this would eliminate the gas pipe as an electrode.
I see it that way as well (notwithstanding any previous comments). The diagram mentions a detail for bonding metal pipes elsewhere on the same sheet, but it is not in our field of view. So it wasn't clear whether the pipes shown on the right side were all internal to the building, as opposed to extending into the dirt outside the building.The way I read the diagram, the column of items on the right are items to be bonded, not electrodes. The rest of the items are grounding electrode system.