I’ve never seen this before, and I’m not sure if it meets code or not.
Main service on a residential building feeds panel in second building (with main breaker) about 40 feet away. Three insulated conductors for 240 volts, two ungrounded and one grounded neutral. So far everything is normal, but the equipment ground is bare solid copper, connects to two ground rods and then continues to the main building, all unspliced, as far as I can tell. So it serves as the grounding electrode conductor and the equipment ground at the same time. No main bonding jumper at the second building, and all conductors in bare earth and run together. Probably worth it to note that this was built about ten years ago, maybe a little more. I really can’t find anywhere where this is a violation, but it looks strange.
Main service on a residential building feeds panel in second building (with main breaker) about 40 feet away. Three insulated conductors for 240 volts, two ungrounded and one grounded neutral. So far everything is normal, but the equipment ground is bare solid copper, connects to two ground rods and then continues to the main building, all unspliced, as far as I can tell. So it serves as the grounding electrode conductor and the equipment ground at the same time. No main bonding jumper at the second building, and all conductors in bare earth and run together. Probably worth it to note that this was built about ten years ago, maybe a little more. I really can’t find anywhere where this is a violation, but it looks strange.