Is this panel to code?

Status
Not open for further replies.

sleuth255

Member
Does the location of this panel meet minimum workspace requirements?

P3261598-vi.jpg


The distance from the wall to the right side of the main panel is 18"
 
Re: Is this panel to code?

yes see section 110.26(A)(2). The width does not have to be centered.
Now the door is another issue.
Whats the violation for?
 
Re: Is this panel to code?

If the panel face is recessed into the opening IMO that causes two violations.

110.26(A)(2) Width of Working Space and 110.26(A)(3)Height of Working Space.
 
Re: Is this panel to code?

It is hard to tell with the picture, but this is a typical installation that we see for existing panels in basements when the basement is finished at a date after the panel was originally installed.
If the panel cover is flush with the wall surface, I do not see a problem. The hinge on the door makes it look as though this may be. The pipe above the panel is in front of the panel and does not create any violations, close but no cigar ;) .
 
Re: Is this panel to code?

Agreed it is a violation but i dought most inspectors would tag it.Looks like someone finished a basement and wanted to hide the panel.I see no real safety hazard with it.
 
Re: Is this panel to code?

Thanks for the info. The panel is indeed recessed about 4 inches into the opening although the right opening panel door goes well beyond the 90 degree requirement. The cover is also easily removed.

However, it would appear that the recess is what causes the violations here. I suppose the only remedy is to either move the panel forward 4" or move 30" of wall backward 4". Are there any other remedies?
 
Re: Is this panel to code?

Jim, it would have been better if you said "I blew the picture up and it looks like maybe 3 inches recessed."

Roger
 
Re: Is this panel to code?

Jim

If you were to become an inspector, one thing you would learn real fast is that "letting it slide" does not work - legally or otherwise. It is not up to the inspector to "let it slide". It is up to the inspector to enforce the code (whichever code that may be) as written.

The OP mentioned that the panel is recessed 4 inches. If you are permitting him the 4 inches, where does that stop. The next guy might want 6 inches, the guy after that says the 10 inches is the best he can do. As you can see this type of situation can easily get out of hand. That is why everyone gets treated the same - fairly - by following code as written.


BTW: I would be hard pressed to have corrections made in the situation pictured here, but I have learned that once all know that they are to follow the code, it is generally understood and they will try. (with a few words mumbled under their breath :( ;) )
 
Re: Is this panel to code?

Originally posted by roger:
Jim, it would have been better if you said "I blew the picture up and it looks like maybe 3 inches recessed."
Now, let's be fair, Roger. It is entirely possible that Jim "blowed the picture up" just as he said. We probably would have enlarged it, however.
 