Is this parallel conductors?

Status
Not open for further replies.

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
With a 10-in-1 in my pocket and some time to kill I could not help but look at some interesting PLC controlled dimmer(s). I was not there for anything work related.
I was surprised to find one solid state dimmer dimming 4 two wire 240V circuits.
There are 4 # 12 conductors all from the same leg of four 2 pole 20's landing on the one line in lug of the dimmer.
From the one line out lug four #12AWG conductors go to separate 240V resistive loads.

At the dimmer the supply conductors are obviously joined. However each supply conductor originates at a different breaker, however all these breakers are joined on the same bus.
If there is a ground fault all four 2 pole would have to trip. In addition all of the 240V receptacles would have 1 leg energized unless all four 2 pole 20's are switched off.

Parallel conductors ? MWBC ?All kinds of code issues come to mind.

The dimmer is rated for the load.
It looks like a clean professional installation, definitely done by a contractor and inspected.
 
IMO you do have parallel conductor to the dimmer. They all originate on different breakers but those breakers are connected to one phase. So, yes they meet the definition of parallel conductors. They do not meet the definition of MWBC.
 
...

Parallel conductors ? MWBC ?All kinds of code issues come to mind.

...
Violation...

240.8 Fuses or Circuit Breakers in Parallel. Fuses and
circuit breakers shall be permitted to be connected in parallel
where they are factory assembled in parallel and listed
as a unit. Individual fuses, circuit breakers, or combinations
thereof shall not otherwise be connected in parallel.
 