fmtjfw
Senior Member
- Location
- Fairmont, WV, USA
225.40 Access to Overcurrent Protective Devices.
Where a feeder overcurrent device is not readily accessible, branch-circuit overcurrent devices shall be installed on the load side, shall be mounted in a readily accessible location, and shall be of a lower ampere rating than the feeder overcurrent device.
Is the idea here that the OCPDs will somehow co-ordinate and the branch circuit will open before the feeder does?
I'm under the impression that in the real world, without some study of trip curves and careful selection of OCPD's, this is not likely to work.
Where a feeder overcurrent device is not readily accessible, branch-circuit overcurrent devices shall be installed on the load side, shall be mounted in a readily accessible location, and shall be of a lower ampere rating than the feeder overcurrent device.
Is the idea here that the OCPDs will somehow co-ordinate and the branch circuit will open before the feeder does?
I'm under the impression that in the real world, without some study of trip curves and careful selection of OCPD's, this is not likely to work.