i was told by 2 masters that this is ok and im still not sure it is. so i figured i would ask the pro's.
can a bath fan be controlled by 2 different timers(1- 24 hr in a closet and 1- 60min in the bath) both are fed by the same branch circut. 2 lines controling the same load.
when 1 is on and the other is off there is still 120v on the load side of the 1 that is off and vice versa however when both are on there is still 120v at the load. is this common practice? as im told by the 2 masters i usally refer to or should i find another job?