I think that was the OP's question, is it required by the NEC. Note 1 has many things that are not required, same with Note 4. Since conduit protection is not required add Note 3 to the list too.IMHO... It might be required by job spec by the customer, or by AHJ, but not required by code.
Maybe, but there is no indication on line drawing as to the length of the run that might need to increase size for voltage drop. Depending on the min size that might be installed then the EGC would be increased proportionally to the increase in the current carrying conductors, so the #1 EGC might be undersized.Two 350 cu seems kind of excessive too.
I think this drawing was done by someone who does not know what they are doing and just made everything overkill to cover that lack of knowledge.
Since there is a 400 amp OCPD and over 600 amps worth of conductors I would say that the ungrounded conductors have been increased in size therefore the #1 may be too small. Given the other errors with this drawing I'm not surprised the designer got that wrong too.Maybe, but there is no indication on line drawing as to the length of the run that might need to increase size for voltage drop. Depending on the min size that might be installed then the EGC would be increased proportionally to the increase in the current carrying conductors, so the #1 EGC might be undersized.
The #1 egc appears to be adequately sized for increase in circular milsso the #1 EGC might be undersized.
I just eyeballed it like Fred, did you do the calculation?The #1 egc appears to be adequately sized for increase in circular mils
Yeah. #1 is 60% larger than #3. 700mcm is only 40% larger than 500mcm.I just eyeballed it like Fred, did you do the calculation?
Thanks for doing the math. Just eyeball like @infinity said. Was throwing out the possibility of oversize for voltage drop and then need to follow up with the EGC increase proportionally. Something most miss.Yeah. #1 is 60% larger than #3. 700mcm is only 40% larger than 500mcm.
For my original eyeball I thought that since this installation uses parallel conductors if you used the minimum required size of parallel #3/0's (400 amps) the #1 is too small when applying 250.122(B). The minimum size would be #4/0. I'm rusty at these calculations so check my math.Just eyeball like @infinity said.
You based it off of the #1 cu.For my original eyeball I thought that since this installation uses parallel conductors if you used the minimum required size of parallel #3/0's (400 amps) the #1 is too small when applying 250.122(B). The minimum size would be #4/0. I'm rusty at these calculations so check my math.
#3/0=167800 cm
3/0*2=335600 cm
350,000*2=700000 cm
700 kcmil/335.6 kcmil = 2.09 ratio of size increase
#1=83690 cm
83690*2.09= 175 kcmil
#3/0= 167.8 kcmil too small
#4/0= 174912 correct size.
Yes you would. As I said a little rusty but my initial guess that the #1 could be too small was accurate. I made the correction to my last post.You based it off of the #1 cu.
Wouldn't you base it off the minimum EGC required for the 400 amp. Which would be #3 cu @ 2.08581 ?
52620* 2.08581= 109,755.3222
2/0@ 133,100 CM