I would tape it and get that pressure off that ground bar, its dug in kinda deep.
Easy fix
Looks like it's only the nylon jacket that's affected so it's probably fine as is.
This is going into a 70A breaker…I believe it is just the jacket as there are a few copper wires coming out of it (not insulated wires) going into the breaker.The nylon jacket plays no part in the dielectric strength of the insulation. I think it is actually removed for the NRTL testing and listing. IOW's, no problem.