A coworker said it’s illegal to mount a transformer high up on a wall since it’s not directly next to its panel or disconnect and isn’t easily accessible for maintenance. I disagreed, since I’ve seen and designed plenty of setups where a transformer is wall-mounted, with the panel or disconnect nearby and accessible.
Example setup:
480/277V Panel -> 150kVA Wall-Mounted Transformer (offset from panels, hosted 6'+ AFF to reduce space consumption) -> 208/120V Panel
I reviewed NEC 450.13, which restricts transformers over 112.5 kVA from being installed in ceilings, floors, or hollow spaces in combustible buildings unless:
-It’s rated 600V or less
-It’s in a vault per 450.41
-It meets ventilation requirements in 450.9
and
450.14 Disconnecting Means. Transformers, other than Class
2 or Class 3 transformers, shall have a disconnecting means located either in sight of the transformer or in a remote location.
Where located in a remote location, the disconnecting means shall be lockable in accordance with 110.25, and its location shall be field marked on the transformer.
In this case, the transformer is under 600V and in an open area and as long as the disconnect is accessible and clearly associated, I believe that satisfies code.
A side note: I assume the same exceptions would apply if this equipment/setup was mounted on any structure (i.e. - uni-strut)?
Thoughts?
Example setup:
480/277V Panel -> 150kVA Wall-Mounted Transformer (offset from panels, hosted 6'+ AFF to reduce space consumption) -> 208/120V Panel
I reviewed NEC 450.13, which restricts transformers over 112.5 kVA from being installed in ceilings, floors, or hollow spaces in combustible buildings unless:
-It’s rated 600V or less
-It’s in a vault per 450.41
-It meets ventilation requirements in 450.9
and
450.14 Disconnecting Means. Transformers, other than Class
2 or Class 3 transformers, shall have a disconnecting means located either in sight of the transformer or in a remote location.
Where located in a remote location, the disconnecting means shall be lockable in accordance with 110.25, and its location shall be field marked on the transformer.
In this case, the transformer is under 600V and in an open area and as long as the disconnect is accessible and clearly associated, I believe that satisfies code.
A side note: I assume the same exceptions would apply if this equipment/setup was mounted on any structure (i.e. - uni-strut)?
Thoughts?