Hi
do you know
why LADWP gives or reports available fault value sometimes more than 50000 amp
but SCE Edison utility company gives 4200 amp maximum

thank yiu
 
Without more details, it could be that LADWP is giving a fault current based on an infinite bus and 50kA would be around a 2500kVA txf with a 480Y/277V secondary. SCE could be giving primary available fault current.

Really need more details.
 
Less liability for them to give someone a high figure in this area than to give a figure that is low, especially if they didn't take the time to actually do the calculations specific to a particular installation.
 