Island backsplash receptacles
I've read and reread 210.52, and I can't find anywhere where the 2' rule applies to island receptacles. I understand that all islands require at least one, and if the counter behind the cooktop or sink (if applicable) is less than 12", then the island would be considered two spaces and therefore at least one receptacle in each space would be required. I have been red tagged on a kitchen with an island that has a backsplash with gfci receptacles on each side of the sink. Inspector wants more, says the 2' rule applies. I understand it to mean that only WALL countertop spaces apply. I could not get a code reference from the inspector as I was told 3rd hand by my boss from the GC from the inspector, and have not yet been able to get hold of the GC.
An island has separate requirements from a counter that is against a wall. The inspector is incorrect. 210.52(C) and (C)(2).
2) Island Countertop Spaces. At least one receptacle shall be installed at each island countertop space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater.
(4) Separate Spaces. Countertop spaces separated by rangetops, refrigerators, or sinks shall be considered as separate countertop spaces in applying the requirements of 210.52(C)(1), (C)(2), and (C)(3).
It spounds as if you comply with min requirements, ask for inspector to cite the violation
I agree with Rob but also look at 210.52(C) (4). Is your inspector thinking that the backsplash is a wall?
Thats the only thing I can think of, or a local code (doubt it). In my opinion, an island with a backsplash in no way meets the definition of a wall. If it did there would be language in 210.52(C) regarding backsplashes. Hopefully a code ref will be forthcoming Monday.
Thanks for the replies.
An island is just that, an island. If it bordered a wall it wouldn't be an island. IMO the NEC is pretty clear on the requirements for an island.